Installation Instructions
Wiser Energy
Safety Precautions
Electrical equipment should be installed, operated, serviced and maintained only by qualified personnel. No responsibility is assumed by Schneider Electric for any consequences arising out of the use of this material.
DANGER
HAZARD OF ELECTRIC SHOCK, EXPLOSION OR ARC FLASH
Apply appropriate personal protective equipment (PPE) and follow safe electrical work practices. See NFPA 70, CSA Z462, or NOM 029-STPS.
This equipment must only be installed and serviced by qualified electrical personnel.
Turn off all power supplying this equipment before working on or inside equipment.
Always use a properly rated voltage sensing device to confirm power is off.
Replace all devices, doors, and covers before turning on power to this equipment.
Beware of potential hazards, and carefully inspect the work area for tools and objects that may have been left inside the equipment.
Failure to follow these instructions will result in death or serious injury.
The Wiser Energy System has been tested and certified for use with Square D™ circuit breakers, load centers and combination service entrance devices (CSEDs) as installed per this manual.
For use in non-Square D load centers and CSEDs please consult with the manufacturer for compatibility.
Specifications
Technical Specifications
Wiser Energy is a home energy monitoring device. It is used to measure the current and voltage on the service mains. The device monitors two phases of 120 VAC. If installed outside, it must be kept dry and within specified temperature ranges.
Current Sensor Specifications
CAT IV 250 V 200 A max
Cable length: 46 in. | Inside diameter: 0.95 in.
May be used on uninsulated conductors
Monitor Specifications
Compatibility: 120 VAC (90 V–130 V)
Power Use: < 5 Watts, 0.1 amps
Wi-Fi: 2.4 GHz 802.11b/g/n
Size: 137 mm x 66 mm x 32 mm
Weight: 200 g
Climate Specifications
RH <90%; IPx0 rating
Temperature: 32 – 154.4 ºF (0 – 68 ºC)
Elevation < 6,561 ft. (<2,000 m)
Legal
This equipment has been tested and found to comply with the limits for a Class B digital device, pursuant to part 15 of the FCC Rules. Operation is subject to these conditions:
1. It may not cause harmful interference.
2. It must accept any interference received, including interference that may cause undesired operation. If it is not installed and used as per the instructions, it may cause interference which is harmful to wireless communications. There is no guarantee that interference will not occur in a particular installation. If it does cause interference we recommend: reorienting or relocating the receiving antenna, or increasing the separation between the device and the receiver.
3. Patents: sense.com/patents
Certified to CSA STD C22.2 No. 61010-1
Conforms to UL STD 2808
Conforms to UL STD 61010-1
Conforms to UL STD 61010-2-032
Conforms to CAN ICES-3(B)/NMB-3(B)
Wiser Energy components
Monitor
Current Sensors
Power Cable
Antenna Assembly
Mounting Bracket (optional)
Instructions
01 Turn OFF power
Installation of the Wiser Energy System requires removal of all power. Be sure to provide an alternate light source before beginning the installation procedures. Do not begin the installation procedures until all power is completely removed from the equipment inlcuding any alternate power sources.
1. Turn OFF the main feeder disconnect that supplies power to the equipment, or if the installation uses the revenue meter for isolation, arrange for the utility provider to remove power. If a main feeder disconnect is not present and the revenue meter cannot be used as an isolation device, contact the utility company for removal of power.
2. Turning OFF only the main circuit breaker is insufficient to remove power completely from the panel. Line side connections will still be live.
3. Apply the appropriate lockouts to the disconnecting means.
4. Turn OFF all alternate power sources connected to the equipment.
02 Remove panel cover
1. Apply appropriate PPE.
2. Remove the cover screws and remove the load center cover.
3. Measure the voltage from each line to neutral and from line to line to confirm that all power is OFF.
03 Find a spot for the Wiser Energy monitor
The Wiser Energy monitor is designed to fit within the main panel in order to monitor a home’s energy consumption.
Note: If there is no open space available, use an external enclosure following NEC® and local standards.
04 Install the antenna
Using the back of a screwdriver, punch out the knockout cover in the electrical panel. Then, insert the antenna.
DANGER
HAZARD OF ELECTRIC SHOCK EXPLOSION, OR ARC FLASH
Maintain 1 in. (25mm) minimum separation between the monitor and antenna extension assembly to load center parts (bus, stabs, circuit breakers, and power wires).
05 Connect
Connect the power cable, antenna, and current sensors to the monitor. Be sure to insert the sensor into the outer port. The middle port is for advanced installations.
06 Clamp sensors around service mains
As a precaution, first plug the sensors into the Wiser Energy monitor.
Clamp the current sensors around the service mains so that both Wiser Energy labels face the same direction. The direction of the labels on the sensors should face the power source. Once placed in the final orientation, push the sensor lock in until you hear a click.
07 Connect the power
(compatible with Square D 15 – 30 A thermal magnetic circuit breakers).
Dedicated Circuit Breaker Method
Add a new Square D brand two-pole 15 – 20 A circuit breaker into the load center. With circuit breaker OFF, connect the black power wire to one circuit breaker terminal and connect the red wire to the other terminal.
Two Wire Rated Lug Method
Existing Square D brand 15 – 30 A thermal magnetic two-pole circuit breakers in the load center have terminals that can accept two conductors. With the circuit breaker OFF, use half of the clamp plate for load wire and the other half for Wiser Energy power wire.
Pigtail Wire Method
With the circuit breaker OFF, create a splice connection to the two-pole circuit breaker following the NEC and circuit breaker manufacturer guidelines for splice connector type and wire size.
Note: For all three methods, attach a white wire to an appropriately sized terminal on the neutral bus bar.
08 Close the panel
Replace the panel cover carefully to ensure that there is no pressure on the current sensor clamps that would cause them to open. Label the Wiser Energy circuit breaker with the included sticker.
09 Turn power ON, wait for chime
Once the panel is closed, restore power to the panel and listen for one minute for one of the following sounds (visit help for troubleshooting).
Success Chime: Installation was successful!
Repeating Beep: There is an installation problem. Check cable connections.
No Sound: The Wiser Energy monitor cannot start. Check power cable connections.
10 Use the application to complete setup
Install the Sense app. Tap “Create Account” and follow the on-screen instructions. The app will guide you through the Wi-Fi setup and account creation process.